I have been trying to determine the response coefficients for seismic analysis of Non building structures in ASCE 7-10 and found that the value of R, the response coefficient, is larger in case steel connections are detailed using AISC-341 than AISC-360, this would imply a larger design load in case of AISC 341 than AISC 360.
So basically,
AISC 341 -> Large seismic design load
AISC 360 -> Smaller seismic design load
Does that imply AISC 341 design results in a more conservative steel connection than AISC 360 or is there a difference in steel design philosophy?
The R-factor reduces seismic design force from the linear-elastic demand. Thus, the larger the R-factor, the lower the seismic design force.
Essentially, we're approximating inelastic seismic design by accounting for the ductility of the structural system. Connections designed per AISC-360 (which does not specifically address seismic design) can be expected to be less ductile than those designed per AISC-341.
So.
AISC-341 = more ductile = higher R = lower seismic design force
AISC-360 = less ductile = lower R = higher seismic design force