This question might sound stupid as I'm more of a software guy and never really had to do control engineering (besides the 101 classes).
So I have a second order system I could approximate, with the following denominator:
$$s^2 + a_1s + a_0$$
Both $a_1$ and $a_0$ are positive, which means, for a 2nd order system, that it is stable.
However this system's input is a motor's command (not a speed but a PWM cycle value), and the output is the robots angle.
Technically, my angle will go to $+\infty$ with a constant input, which means my system will never stabilize. So the system should not be stable.
Besides, plotting my transfer function's output to a constant input using scipy gives me the expected result (an angle which ends up growing linearly as the speed stabilizes).
So what am I missing here? Is my model completely wrong? Or did I miss something on the definition of "stability" itself? It would make sense if I worked on the speed but the variable I work on is the angle.
    $\begingroup$ The denominator is $s \left(\text{a0}+\text{a1} s+s^2\right)$. Are you sure there is no $\frac{1}{s}$ in your loop. $\endgroup$ – Suba Thomas May 31 '16 at 15:00
  • $\begingroup$ No there's no 1/s. I actually found that the system's response is really slow, and it ends up stabilizing. I guess my estimation is still usuable in that case, although I will never reach the stability point ? (and although the system is technically unstable) $\endgroup$ – lesurp May 31 '16 at 15:30
    $\begingroup$ I'm a bit surprised. Typically, the transfer function from voltage (pwm) to speed is second order, and that from voltage to angle is third order with the third pole at the origin $\frac{1}{s}$. $\endgroup$ – Suba Thomas May 31 '16 at 16:04
  • $\begingroup$ Well my supervisor told me to work with the equation $$ d^2phi/dt^2 = -a_1*d phi /dt - a_0phi + b*u(t) $$ With phi being the angle, and u the PWM's duty cycle. $\endgroup$ – lesurp Jun 1 '16 at 11:27
  • 3
    $\begingroup$ With the equation from your supervisor, $\phi$ will not go to $\infty$ for constant u. $\endgroup$ – Suba Thomas Jun 1 '16 at 20:26
Without any more info, I think your problem arises from the values of $a_0$ and $a_1$. The answer is a little involved, so a bit of systems background is necessary.
The short answer
Your system should be stable, but I don't think you are simulating your system long enough to see it stabilize. Calculate your settling time and simulate it for at least that long to see the complete response transient.
The long answer
The characteristic equation (i.e. denominator of the transfer function) of a general 2nd order system has the following convenient form:
$s^2 + 2 \zeta \omega_n s + w_n^2 $
In this form, $\zeta$ is known as the damping ratio and $\omega_n$ is the natural frequency. As you noted this system is guaranteed to be stable if $w_n^2 > 0$ and $2 \zeta \omega_n > 0$.
In systems engineering we have several rules of thumb for determining the transient response of such systems. One of these is called the settling time $t_s$. It is a measure of how long it takes for the amplitude of the system's oscillations to decrease below a certain threshold, usually 2% or 5% of the steady state value (i.e. the value at which the system stabilizes). You can calculate your settling time using the following approximation (this one is for the 2% criterion):
$t_s = \frac{4}{\zeta \omega_n}$
Therefore, if you do not simulate your system until the settling time, you may see a system that does not appear to stabilize. Note that if $\omega_n$ is very small (therefore your $a_0$ parameter is very small) the settling time could be very long.
For your reference, you can calculate $\omega_n$ and $\zeta$ from your parameters via the following:
$\omega_n = \sqrt{a_0} \qquad \zeta = \frac{a_1}{2 \omega_n}$
A demonstration
Check out what happens when I simulate a second order system with $\omega_n = 0.01$ rad/s and $\zeta = 0.9$ (i.e. $a_0 = 0.0001$ and $a_1 = 0.0180$). Its settling time is approximately 444 seconds. The initial conditions are $\phi = 0$ and $\frac{d\phi}{dt} = 0$. I applied a unit step input (i.e. a constant motor input equal to 1). The following figures show the same system with the exact same conditions, but simulated for different lengths of time. This was all done in MATLAB Simulink, my preferred math simulator.
Simulating for too little time
Simulating for an appropriate amount of time
As you can see in the first image it appears that my system is unstable, but in the second image it becomes clear that it is simply taking a very long time to stabilize.
I hope this helps.
| improve this answer | |
    $\begingroup$ +1 for an excellent first post! This is exactly the level of quality that we like to see. $\endgroup$ – Chris Mueller Jun 3 '16 at 18:46
  • $\begingroup$ @BarbalatsDilemma thanks, it was indeed because the system is really slow to stabilize. I forgot to edit my post to say that I actually found it stabilizes after 200+ seconds. My a0 and a1 were low (only ten times higher than the values you used). My supervisor told my a0 should actually be 0 (and my value is just errors) which makes sense because my angle cannot be determined solely thanks to my differential equation (my system doesnt have a "default" angle it will aim at even with a null speed/acceleration/command). $\endgroup$ – lesurp Jun 4 '16 at 20:13
I'm also a software guy and not completely master of the subject, but I tried to model your system. Each step is shown, so you can catch mistakes I did.
Here is the schematic diagram of DC motor: DC Motor Schematic Diagram
Kirchoff's voltage law for electrical circuit: \begin{equation}\label{eq:kirchoff} \tag{1} V_s = V_l + V_r + V_e \\ \end{equation}
Newton's $2^{nd}$ law of motion: \begin{equation}\label{eq:newton} \tag{2} \sum{F} = ma \end{equation}
Equation for Electro-Motive-Force (EMF): \begin{equation}\label{eq:emf} \tag{3} V_e = K_e \dot{\theta} \end{equation}
Equation for electro-mechanical convertion of tourque: \begin{equation}\label{eq:torque} \tag{4} \tau = K_ti \end{equation}
Using equations \ref{eq:kirchoff} & \ref{eq:emf}: $$ u(t) = L \frac{di}{dt} + R i + K_e \dot\theta $$
Using equations \ref{eq:newton} & \ref{eq:torque}: $$ K_t i = J \ddot\theta $$ Laplace transfer of equations: $$ U(s) = s L I(s) + R I(s) + s K_e \Theta(s) \\ K_t I(s) = s^2 J \Theta(s) $$ $I(s)$ is common: $$ I(s) = \frac{U(s) - s K_e \Theta(s)}{s L + R } \\ I(s) = \frac{s^2 J \Theta(s)}{K_t} $$
$$ \frac{U(s) - s K_e \Theta(s)}{s L + R } = \frac{s^2 J \Theta(s)}{K_t} \\ K_t U(s) - s K_t K_e \Theta(s) = s^3 J L \Theta(s) + s^2 J R \Theta(s) \\ K_t U(s) = s^3 J L \Theta(s) + s^2 J R \Theta(s) - s K_t K_e \Theta(s) \\ K_t U(s) = \Theta(s) ( s^3 J L + s^2 J R - s K_t K_e ) $$
Transfer function of system with voltage input and position output: $$ \frac{\Theta(s)}{U(s)} = \frac{K_t}{s^3 J L + s^2 J R - s K_t K_e} $$
If we want to investigate voltage-speed relationship: $$ s(\frac{\Theta(s)}{U(s)}) = s(\frac{K_t}{s^3 J L + s^2 J R - s K_t K_e}) \\ \frac{s\Theta(s)}{U(s)} = \frac{K_t}{s^2 J L + s J R - K_t K_e}) $$
Applying step input, which is PWM with 100% duty cycle: $$ \Theta(s) = \frac{\alpha}{s} \frac{K_t}{(s^3 J L + s^2 J R - s K_t K_e)} $$
It might be good to investigate stability of a system with impulse input instead of step input.
With mobility analogy, Voltage & Velocity are cross variables, Current & Force are through variables, you can also investigate the system as RLC series circuit as shown below. RLC Series Circuit
For $u(t)$ input $V_c$ output, it is voltage-velocity relation and $u(t)$ input $\int{v_c(t)dt}$ for voltage-position relation. So it adds 1 more degree to your system.
Voltage-Velocity Relation