A textbook is attempting to convince me that the following figure:
Represents the generic zones for a Case B wind loading including roof overhangs based on the ASCE 7-10 Chapter 28, Part 2 (Enclosed Simple Diaphragm Low-Rise Buildings) procedure. This procedure addresses roof overhangs via footnote 8 on Figure 28.6-1:
"Where zone E or G falls on a roof overhang on the windward side of the building, use EOH and GOH f`or the pressure on the horizontal projection of the overhang. Overhangs on the leeward and side edges shall have the basic zone pressure applied."
I absolutely do not agree that the figure is a correct application of the Chapter 28, Part 2 wind loading provisions for Case B wind direction. Please see below for ASCE 7-10 Figure 28.6-1 Case B zoning. You may observe that zones H, E , A and C correspond, while zones G and F have been flipped.
I would like to know if the textbook is not applying the wind provisions properly, or if I am missing something in the code? Thanks.
Assuming ASCE 7-10 Figure 28.6-1 is correct and footnote 8 applies, I believe the following (edited) figure shows the correct distribution.