Suppose we craft a reinforced concrete pylon for a cable-stayed bridge. It's very tall and rather thin. No one builds falsework for the entire pylon - it'd be very impractical. Instead, a part of falsework is built for the lowest part of the pylon, filled with concrete, then some time later that falsework is removed and the next part is built for the higher part of the pylon.
So the pylon in not really a single piece of concrete, it a combination of pieces seamlessly united together because the concrete surface of the earlier part is kept clean until falsework is moved up and so new portion of concrete just sticks to it pretty well.
How "monolitic" is such monolitic concrete? How much does it differ from concrete put into falsework size of the entire structure?
  • $\begingroup$ "so new portion of concrete just sticks to it pretty well" is misleading. The two pieces also usually have common rebar that is left sticking out of the first piece. $\endgroup$ Jan 18, 2016 at 13:09
  • $\begingroup$ @ChrisMueller Yes, but now amount of rebar helps if you paint the earlier concrete with alkyd paint. $\endgroup$
    – sharptooth
    Jan 18, 2016 at 13:12
    $\begingroup$ I believe that when one layer of concrete has set before the next layer is poured it is known as a 'cold joint.' You will find plenty of literature about them, but the general point is that if they are planned for (w/ continuity of rebar and rough surfaces) they aren't a big deal, but if they happen unexpectedly at a bad location, they can be a problem. $\endgroup$
    – Ethan48
    Jan 18, 2016 at 14:18
    $\begingroup$ I'm resisting the urge to change the title of this question to "Can concrete poured in multiple stages be considered monolithic?". I think it better describes the question, but it's not as if the current title is wrong, so I don't feel comfortable going for it. $\endgroup$
    – Wasabi
    Jan 18, 2016 at 15:39
  • $\begingroup$ Also consider that most concrete codes require some sort of roughening or other processing at a cold joint in concrete so the subsequent layer can "stick" to the previous one. $\endgroup$
    – grfrazee
    Jan 18, 2016 at 15:45
In a continuous structure such as a beam or a column (under the expected loads for such elements), the structure is effectively indistinguishable from a truly monolithic one.
This has to do with how the elements are poured, with joints perpendicular (or at least not parallel) to the load direction. Columns are poured so that the joints are horizontal, while the load is primarily vertical. Whatever horizontal loads there may be (due to wind, for example) are usually relevant for bending. But in bending the column suffers tension, which the protruding rebar with sufficient anchorage length in both the new and old concrete absorbs, and compression, which is perfectly transferred from one concrete surface to another since the joint is perpendicular to the force.
Very long beams requiring multiple pours are set with joints which are inclined at shallow angles in order to avoid creating a preferential plane for shear forces. One shouldn't make the joints horizontal, though, since that risks the different segments (more like layers) working independently instead of as a monolithic whole. Therefore, the same reasoning given above for the column applies to the beam as well: it suffers mostly bending, where the resultant tension is absorbed by the appropriately-anchored rebar and the compression is resisted by simple transfer between the concrete surfaces.
Now, pre-cast beams are often placed over consoles as in the figure below. Consoles, unlike cantilevers, suffer almost exclusively shear forces and must therefore have "shear friction" reinforcements. The book Design of Concrete Structures (as well as many others) has a description of the method in section 4.9 (pg 160). In new structures these consoles (and the column core between them, of course) should be poured all at once to avoid any joints. That being said, this isn't always possible. If you are reinforcing an existing structure, you might need to create such a console on a column which doesn't have one. You therefore have to deal with a joint between the new concrete of your console and the old concrete of the existing structure. This is an obvious problem since it creates a preferential shearing plane. The shear friction method considers such cases with a friction coefficient $\mu$ which is a function of the type of shearing plane (fully monolithic; new concrete on old, roughened concrete; new concrete on old, non-roughened concrete; steel on concrete). The book linked above has the appropriate coefficients listed on pg 161.
enter image description here Source
This shows that, yes, pour-joints may have an influence on the behavior of the structure if they are parallel (or close enough) to the direction of the load. If a beam were poured with vertical joints, it would create a preferential shear plane which would be quite tricky to reinforce. If a partially-loaded column (where the axial load is concentrated in a sub-region of the column's head) were absurdly poured with vertical joints, Saint-Venant's Principle may not really apply and the load may not be adequately distributed to segments of the column not directly under the loaded region.
In the specific case of the pylon mentioned in your question, I'm unsure since I've never designed one myself. As a first guess I'd consider it worrisome to create a horizontal joint near one of the cable anchors since that region must suffer significant shear forces which would be near-parallel enough to make me nervous about the joint behaving as a shearing plane. My completely ignorant, zero-experience approach would be to plan the joints so as to maximize the smallest distance between a joint and a cable. Also, maybe make the joints inclined so as to increase the angle between the cables and the joint (I don't even know if that's plausible in this case). Maybe both.