6
$\begingroup$

This is the situation - I have three heat sources, called CHP, burner 1 and burner 2 on the same circuit. All three feed to the same heating manifold, with various heat demands.

Preferably I want to heat with the CHP; if that is not sufficient, additionally with burner 1; and only use burner 2 if that is still insufficient. The CHP is always running and not controlled for temperature.

The reason for this scheme is that the CHP burns (free) sewage gas and earns money (electricity), burner 1 burns sewage gas and burner 2 uses (expensive) natural gas. Burner 2 is installed in case all other heat providers fail or the sewage gas runs out.

Here's my idea for a control scheme, where the actual temperatures are more examples than set in stone:

  • In normal operation, the return flow is 75 °C or higher
  • If return temp. < 73 °C, burner 1 is activated and heat controlled to 73 °C return
  • If return temp. < 71 °C, burner 2 is activated and heat controlled to 71 °C return

In the last case, burner 1 should run at nominal power and burner 2 at enough power to raise return temp. to 71 °C.

Will I run into problems with two burners on the same circuit controlling for different temperatures?

$\endgroup$
  • $\begingroup$ is the question more related to the circuitry (like driving an electric current interface,etc) or more towards the algorithm and its usefullnes.. the first point I noticed is that even when CHP is first started (after first installation or after some power interruption etc), burner 1 and burner 2 will start and work together if the Return temp < 71deg. $\endgroup$ – Gürkan Çetin Dec 16 '15 at 20:07
  • $\begingroup$ The algorithm and it's usefulness in that specif scenario, and possibly hydraulic problems that I fail to see right now. Given the thermal power of all the devices and the max. heat demand, t<71 will only happen when the CHP is out for some reason. $\endgroup$ – mart Dec 16 '15 at 20:49
2
$\begingroup$

Your control logic appears to be sound. And with that logic, they could each be on separate simple thermostats if necessary. Just make sure all of your temperature sensors are sensing at the same location; or lots of craziness will happen. If you would like us to review your hydraulic plumbing you will need to attach a plumbing diagram.

One important thing to consider is that your thermostats will have a dead band. More expensive thermostats may have an adjustable dead band.

Dead band is the difference between when a controller starts and stops. So in your scenario burner 1 will start at 73 °C and will turn off at (possibly) 74 °C. This gives you a dead band of 1 °C. Depending on the thermal mass of your system, 1 °C may mean a cycle time of 1 hour or 30 seconds. If it is the latter; your themostat, relays and other hardware will wear out quickly so you will want to increase the amount of thermal mass or dead band.

Overlapping them would not necessarily be a bad thing; and would help the system quickly return to the 75 °C set point after a large load. Your choice here depends on how critical the 75 °C target is and how expensive fuel is.

Burner 1 on when between 73 °C and 75 °C
Burner 2 on when between 71 °C and 75 °C

You will also want to add some sort of notification system like an led to let you know when Burner 2 is on and that it is costing you money. Thermostats, relays, and temperature sensors do go bad. It would be nice to know if the system is acting up before the bill at the end of the month.

| improve this answer | |
$\endgroup$
  • $\begingroup$ "dead band" <--> "hysteresis" . Just pointing that out so if the OP does what he should and get a book on control loop theory, he can understand the terms. $\endgroup$ – Carl Witthoft Dec 17 '15 at 12:38
  • $\begingroup$ @CarlWitthoft, I don't think for this simple of application a book on control loop theory would be required. I agree with you on the vocab issue. I was hesitant on which one to use. Both have more complex meanings that get muddled in this simple system. I did not find any consistency in a brief internet search. Maybe I will post it as a question this evening. $\endgroup$ – ericnutsch Dec 18 '15 at 0:57
  • $\begingroup$ @CarlWitthoft, I posted that question if you are interested. engineering.stackexchange.com/questions/6576/… $\endgroup$ – ericnutsch Dec 18 '15 at 5:09
0
$\begingroup$

"Will run into problems" is a loaded question. If you properly design logic you should not encounter problems. But there are various types of temperature controllers in market that can help you avoid problems. Although not directly applicable, I am mostly familiar with Watlow temperature controllers and some insights into omega temperature controllers which are used in environmental chambers which perform similar functions. I suggest taking a look at these type of controllers because they offer out of the box solutions. Each vendor has different functions, features, and definitions but at a high level the following are the most common:

  1. On-Off controllers
  2. Proportional Controllers
  3. Proportional plus integral controllers
  4. Proportional plus integral plus derivative (PID) controllers

Bellow are some excerpts from Watlow user guide that might be of interest

On-Off controllers

On-Off Controller

Proportional Controllers

Proportional Controllers

Proportional plus integral (PI) controllers

Proportional plus integral controllers

Proportional plus integral plus derivative (PID) controllers

Proportional plus integral plus derivative controllers

Using functions and features available in these controller you will able avoid common problems.


References: