The forward path of your control diagram consists of the following transfer functions connected in series:
$$ \begin{align*} G(s) &= \frac{s+8}{s^2-2s-3}\rightarrow \text{Plant}\\
K(s) &= K \rightarrow \text{Controller} \end{align*} $$
The Loop Transfer Function then is (by considering all other components' dynamics equal to $1$):
$$ L(s) = K\cdot \frac{s+8}{s^2-2s-3} $$
and then the closed loop transfer function with negative unity feedback is:
$$ \begin{align*} T(s) &= \frac{L(s)}{1+L(s)} \Rightarrow \\
\Rightarrow T(s) = K\cdot &\frac{s+8}{s^2+s\cdot (K-2)+(8K-3)} \end{align*} $$
Now, one way of determining the conditions that should be met in order to establish stability of the closed loop system is by using the Routh-Hurwitz criterion. The characteristic polynomial of the closed loop is the denominator of the closed loop transfer function i.e. $P(s) = s^2+s\cdot (K-2)+(8K-3)$. The application of the criterion is as follows:
$$\begin{matrix}s^2 & 1 & 8K-3 & 0 \\
s^1 & K-2 & 0 \\
s^0 & 8K-3 \end{matrix} $$
The criterion says (really in short) that in order for the polynomial $P(s)$ to be stable all the terms of the first column of the Routh table should be homonymous, either positive or negative. I encourage you to study more in depth this criterion. There are many books in which you can find detailed analysis of it . This means that the following conditions should be met:
$$\begin{align*} 1&>0 \\
K-2 &> 0 \Rightarrow K>2 \\
8K-3 &> 0 \Rightarrow K>\frac{3}{8} \end{align*} $$
So, for $K>2$ the closed loop system is stable. This can be validated by simulating the system in MATLAB. The following figures of the system's step response demonstrate this. In the first figure $K=1.99<2$ and the system blows to infinity whereas in the second figure $K=2.01>2$ and the system stabilises (despite the awful performance) itself to $1$.
When talking about root locus bear in mind that the Routh-Hurwitz criterion is a common way of finding the points where the locus crosses the imaginary axis.
I wrote and described the whole answer only because it is your first time posting here. Otherwise, be aware of the fact that you should show some work regarding your question and then the community will help you.