Two tanks with three continuos, redundant level sensors each need to be supervised so that when a certain total volume is reached, a specific actor is triggered. This could be done via the installed PLC system, however it is likely that a regulatory body will demand a hardware solution. However SIL compliance is not demanded. The important thing is that it's hard to alter the function or change parameters.
So I need a device that can do the following:
  • Take average from three analog signals for tank 1, add offset
  • same for tank 2
  • add both values and give a digital signal to trigger if total exceeds a certain value
  • don't add value for tank 1 or 2 to the total, if a maintenance switch assigned to this tank is on
Can this be done in a logic module? If so what specifications (not the specific model) do I need? If not, what's the device called and how to specify?
  • $\begingroup$ Can you please tell us more about the redundant level sensors? Is it possible to share a picture or sketch of the tank? What are electrical characteristics of the three analog signals? $\endgroup$ Sep 3 '21 at 12:19
  • $\begingroup$ no picture, just three sensors measuring essentially the same level $\endgroup$
    – mart
    Sep 3 '21 at 12:24
  • $\begingroup$ How about electrical characteristics of the three analog signals from the sensors? $\endgroup$ Sep 3 '21 at 12:27
  • $\begingroup$ You can use op amps to add the signals, or you could use a parallel output ADC (if those still exist) followed by a whole bunch of logic chips. Neither is a very elegant solution. $\endgroup$
    – Drew
    Sep 4 '21 at 1:41
  • $\begingroup$ 4-20 mA each. I need a prepackaged solution. $\endgroup$
    – mart
    Sep 4 '21 at 19:58
All the major industrial PLC manufacturers make micro PLCs.
Figure 1. Siemens LOGO! base module with built-in HMI and keypad. A larger panel-mounted remote display is available.
The base unit has up to four analog inputs which are 0 - 10 V. You may require 3 × 2-channel 4 - 20 mA analog input modules.
Figure 2. Most of the program requirements done for Siemens LOGO! using Logosoft Comfort and running in the simulator. Download over Ethernet. Double-click for full size view.
  • The analog inputs go through an analog amplifier for scaling. The AM (analog markers) are required to terminate the analog signal as far as I can remember.
  • AVERAGE 1 takes sums the three analog signals and divides by 3.
  • The SUM block sums TANK 1 and TANK 2.
  • The COMPARE block compares against the setpoint. I've added some hysteresis.
The only thing left for you is to add in some MUX (multiplexor) blocks to output a zero if the maintenance switch is on.
I strongly recommend that you avoid hobby boards for industrial controls. PLCs are hardened for industrial environments, have proper isolation between inputs / outputs and control and are very reliable and have a large userbase.
If there is any danger to personnel or property then you need a fail-safe system or fail-safe backup system in conjunction with the PLC. Once you install this you will be liable.
  • $\begingroup$ How would you tamper proof a micro plc? $\endgroup$
    – mart
    Sep 7 '21 at 8:54
    $\begingroup$ Use password protection. The Siemens LOGO! series have it. $\endgroup$
    – Transistor
    Sep 7 '21 at 9:27
Take a look at Analog input modules from National Instruments similar to the one below.
This is prepackaged solution Labview software controlled solution.
Another good place to look at is hobby electronic market.
Some suggestion are
Based on the information provided either of the above will be able assist in achieving your end goal. All of the above have the ability to accept analog inputs.