Picture of a High Voltage Direct Curent powerline (HVDC line) on the Læsø Island, Denmark (from Google Street View): enter image description here
We can observe that there are 2 conductor cables, and that both are insulated from the tower (which is grounded). Because the line is in DC it makes sense to have 2 cables.
However, I see no reason why one of those conductors would not be grounded. For example on railway electrification, one of the conductors (the overhead line or 3rd rail) is always isolated and the other of the conductors is the rail track itself and is grounded.
Grounding one of the conductors on the HVDC line might save money on isolators, not to mention electric and safety issues if the HVDC line as a whole recieves a too large voltage offset compared to ground.
  • $\begingroup$ The ground resistance is higher especially in areas with mountains etc. $\endgroup$
    May 3, 2021 at 10:06
  • $\begingroup$ Might also be an element of EMI sensitivity here (vs lightning, solar flares, other EMP)... the two lines can cross over in tower position periodically like a very large scale twisted pair. I believe this is done with HV 3phase. Alternatively the two lines could be used for redundancy, connected together periodically, so if a span in one line is lost from some accident, the whole line can survive at half capacity. Obv couldn't ground anything in that scenario. $\endgroup$
    – Pete W
    May 3, 2021 at 13:34
Because they're both live
Just because you see multiple wires doesn't mean they are carrying different things. They are frequently paralleled for more ampacity.
It's perfectly common in HVDC lines to use earth as the return path. For instance, the Pacific Intertie does just that, with absolutely massive grounding electrodes at each end.
The grounding system at Celilo consists of 1,067 cast iron anodes buried in a two-foot (60 cm) trench of petroleum coke, which behaves as an electrode, arranged in a ring of 2.0 miles (3,255 m) circumference at Rice Flats (near Rice, Oregon).
The Sylmar grounding system is a line of 24 silicon-iron alloy electrodes submerged in the Pacific Ocean at Will Rogers State Beach[5] suspended in concrete enclosures about 2 to 3 feet (0.5 to 1 m) above the ocean floor.
In that case, the multiple wires on the pole are all live, typically configured as redundant paths so the route is not entirely downed if one wire takes a hit.
The Konti-Skan HVDC line you are talking about does exactly the same thing, although it varies, using a number of methods. In some places it does carry the ground wire on the towers, but on top and insulated from the towers.
Before the implementation of Konti–Skan 2 both conductors were switched parallel, today one conductor is used for the high voltage pole of Konti–Skan 1, while the other is used by that of Konti–Skan 2.
The multiple conductors are either redundant or have different destinations.
9
  • $\begingroup$ That's for the edit StainlessSteelRat. When I try to do that I'm all Elbows ;) $\endgroup$ May 4, 2021 at 3:25
  • $\begingroup$ So there is so much current that the wires themselves, despite being good conductors, get hot; while at the same time the earth is enough conductive to serve as a return path ?! $\endgroup$
    – Bregalad
    May 4, 2021 at 7:16
  • $\begingroup$ @Bregalad Yeah, a high tension line might be 2500 kcmil AAC or 1750 ACSR, and you can look up the resistance of that stuff. Not quite zero, and when you multiply it by hundreds of miles it adds up. $\endgroup$ May 4, 2021 at 7:35
  • $\begingroup$ @Bregalad "Hot" in the answer does not refer to temperature but to the fact that these are working (line voltage) conductors, not neutral (nearly-grounded) conductors. $\endgroup$
    – TooTea
    May 4, 2021 at 7:50
    $\begingroup$ @ChrisH phases are a thing in DC. The whole reason the US has the split-phase system is Thomas Edison aggressively built out a DC system of +110V and -110V with a center common/neutral. When AC won and the Edison systems were converting to AC, doing split-phase AC was the most expedient way to avoid rewiring people's homes. $\endgroup$ May 4, 2021 at 22:49
There are a few possible reasons.
  • Elimination of electrolysis problems with ground connections.
  • Elimination of variations in ground resistance.
Grounding one of the conductors on the HVDC line might save money on isolators, ...
  • Using a ±½VDC on each wire is common. If transmitting, say, 500 kV DC then one wire is +250 kV DC and the other is -250 kV DC. While this may use the same number of insulators split between the two lines, it halves the maximum insulation and clearance distances required and gives a more balanced system.
  • The AC/DC/AC conversion electronics run at half the voltage.
... not to mention electric and safety issues if the HVDC line as a whole receives a too large voltage offset compared to ground.
I'm not too sure what this means. Clarify and I'll try to answer.
... on railway electrification, one of the conductors (the overhead line or 3rd rail) is always isolated and the other of the conductors is the rail track itself and is grounded.
Have another look and I think you'll find that there is a dedicated ground return wire on all systems bonded periodically to the track. Corrosion of buried metal pipelines (water and gas), bridges, tunnel linings, etc., is a major problem that railways have to avoid. This would be a similar problem in an earth return system.