Imagine you are in the mountains and it is very cold. The walls are colder than the air, so air close to the wall will lose heat to the wall, and by losing heat it might lose its humidity (water condenses to the wall). Now I know this is bad for the paint on the wall. However, in some sense, it is heating up the wall, which will lessen the cooling effect of the air. Please tell me if my logic is correct. Also, if the walls are now wet, could they allow for more condensation? Or it is impossible because all the surface is covered in water? PS: House without heating nor insulation.
  • $\begingroup$ Built walls with insulation (30cm approx 1 foot) and a vapor barrier that don't have a problem either inside or outside. $\endgroup$
    Commented Jan 23, 2020 at 14:30
  • $\begingroup$ I am asking for a poor house without insulation nor heating $\endgroup$
    – Mike Harb
    Commented Jan 23, 2020 at 14:32
Certainly we could calculate the heat gain to the wall due to condensation (a glass of ice water will melt faster in humid climates due to the heat gain from condensation).
In practice, though, this will be insignificant compared to typical winter cooling loads. Also, you will never heat the wall above the dew point of the air (temperature at which water condenses out of the air), which is likely in winter to be quite low.
You will never be able to actually heat the room this way because to heat the room you need the temperature of the wall to be above the temperature of the air in the room (heat always moves from high temperature to low temperature). Once the wall is hotter than the air next to it, no water will ever condense from the air.
One consideration that is being overlooked in your description is mass. The mass of the wall and the mass of the cold mountain are substantially greater than the mass of air that is in contact with the wall.
Additionally, the air will have convection currents, which will move the airflow in such a way as to bring new moist air into contact with the wet wall. The wet wall also is subject to gravity, causing the water to flow downward, making available convection and conduction for the "incoming" air. There's really no limit to the condensation relative to "heating" the wall, if the outside temperature remains lower.
As long as there is a disparity of temperature between the outside and inside of the house, there will be airflow and depending on the relative humidity, condensation. If there is no influx of drier air to the house, the condensation may cease.
  • $\begingroup$ Would it be a feasible design to use this condensation as a way to heat the room? $\endgroup$
    – Mike Harb
    Commented Jan 23, 2020 at 15:35
  • $\begingroup$ The energy (heat) contained within the water vapor is being transferred to the wall and to the outside during the condensation process. Energy seeks equilibrium. To heat the room, you have to add energy from another source. Without insulation, you'd be moving more energy outside. $\endgroup$
    – fred_dot_u
    Commented Jan 23, 2020 at 17:52