From a straightforward, academic perspective (by which I mean disconsidering seismic and other code-enforced conditions), your approach is either exactly or roughly correct (depending on your definition, as described below).
Obviously, you must first calculate the entire structure and determine all the internal forces. As you've stated, that will include both the loads directly applied to BE but also any nodal loads transmitted to BE from the columns. This will give allow you to make a perfectly accurate representation of the internal forces on the beam and therefore of the deflections it faces "in isolation".
However, what your analysis is currently missing is that the beam actually isn't in isolation. It belongs to a larger structure which is also deforming, and this deformation also applies what can be effectively considered an imposed displacement to the nodes.
In this particular case, both nodes of BE will be moved to the right, while the left-most node will also move up and the right-most node, down. This means that BE's "straight line representation" in the deformed configuration is actually slanted.
And so it becomes a matter of definitions and possibly codes. What is the deflection to be considered when checking the servicibility limit state?
I'm Brazilian and therefore follow code NBR 6118 for concrete structures and NBR 8800 for steel structures. Both of these1 are unclear as to which deflection to use, stating only that elements should be "analysed as isolated, simply-supported beams under loading"2. I interpret this as allowing your method of disconsidering imposed deflections, but it's not air-tight (imposed deflection could be considered a load, but they do use the word "isolated"...).
Another interpretation is to consider the relative displacement of the nodes: both nodes drop by some amount, but that cancels out, so the only thing that might increase users' unease (the basis for SLS) is the additional deflection of one of the nodes.
Or you might want to consider the total deflection of both nodes: after all, if your columns are very "compressible", your users might become uncomfortable if high variable loading causes the ceiling to drop by half a meter.
That depends on your relevant code (and possibly how you interpret it). If you need to consider these imposed deflections, then you're basically forced to use the stiffness matrix method: you can certainly do it by hand, but it'll just give you a headache.
See below the model I used to look at this problem, and the three ways you can interpret the deflection of BE:
- The top isolated beam is your method, ignoring the imposed displacements
- The middle beam adopts the relative displacement of the nodes, concentrated on the right node
- The bottom beam adopts the full displacement of both nodes and is equivalent to the actual result obtained from the frame (the slight discrepancy is a rounding error due to my inputs).

1 and therefore the Eurocode as well, since they're the inspiration for the Brazilian codes
2 That's my own literal translation from the Portuguese.
Diagrams obtained with Ftool, a free 2D frame analysis program.