According to ACI the stiffness modifier for moment of inertia for flat plate and flat slabs is 0.25 (ACI318/318R-02 10.11.1) to mitigate for the cracked section.
But in a prestressed slab (post-tensioned) the crack is controlled can the stiffness modifiers be taken higher than 0.25?
My professor suggests that it could be taken between 0.6-0.8, can anyone suggest any article or document or even a discussion about this topic to be sure about this problem ?
The Los Angeles Tall Buildings Structural Design Council (LATBSDC) 2017 guidelines suggest using the following (Table 3, LATBSDC 2017):
Service-Level Evaluation:
  • Axial : $0.8E_cA_g$
  • Flexural : $0.8E_cI_g$
  • Shear : $0.4E_cA_g$
MCE-Level Evaluation:
  • Axial : $0.5E_cA_g$
  • Flexural : $0.5E_cI_g$
  • Shear : $0.2E_cA_g$
For code-level evaluation you could use some value between those two, as you professor recommended. However, it is common practice to use the full section for PT slabs (i.e., modifier = 1.0).