I know that the closed-loop transfer function is equal to Y/Ysp = (P controller * DC motor) /(1+(P controller * DC motor)) then I am struck. Can anyone give me some hints on how to proceed?
1 Answer
You don't need to use the transfer function for this problem, just substitute the known equations in the time domain to get a differential equation for the closed loop. You have
$$ V(t) = K_p e(t) \qquad e = Y_{sp} - Y(t) \qquad \tau_L = 0$$ $$ T \frac{d^2Y(t)}{dt^2} + \frac{dY(t)}{dt} = K V(t) - K_B \tau_L(t)$$
Just insert the first three equations into the fourth and you have your closed loop differential equation.
$$ T \frac{d^2Y(t)}{dt^2} + \frac{dY(t)}{dt} = K K_p (Y_{sp} - Y(t))$$
Rearrange to get into the standard differential equation form with your states on the left-hand-side and your inputs on the right-hand-side:
$$ T \frac{d^2Y(t)}{dt^2} + \frac{dY(t)}{dt} + K K_p Y(t) = K K_p Y_{sp}$$
Now you can analyze the control system as a simple second-order DE with a constant input.
Edit: Steady state value
The steady state value can easily be derived from the differential equation. We know that when the system reaches steady state, by definition, $\frac{d^2Y(t)}{dt^2} = 0$ and $\frac{dY(t)}{dt} = 0$. Therefore, substituting those values in the DE and setting $Y(t)=Y_{ss}$:
$$ T \cdot 0 + 0 + K K_p Y_{ss} = K K_p Y_{sp}$$ $$Y_{ss} = Y_{sp}$$
$\begingroup$ Hi . Thanks for your help. Could I check with you now that Ysp has changed (let's said it increase) , how will it affect the response? Is there some guideline to check these response? $\endgroup$ Commented Feb 27, 2017 at 19:08
$\begingroup$ @LearningLaSo if $Y_{sp}$ changes then the system will respond according to the differential equation. I don't know what exactly it is you want to know $\endgroup$ Commented Feb 27, 2017 at 22:12
$\begingroup$ Hmm what I mean how do I check the steady state response based on the second order system equation? $\endgroup$ Commented Feb 28, 2017 at 0:09
$\begingroup$ I can Laplace transform it but I am not sure what the initial condition is. $\endgroup$ Commented Feb 28, 2017 at 0:24
$\begingroup$ @LearningLaSo The steady state value of a linear system is independent of the initial condition $\endgroup$ Commented Feb 28, 2017 at 3:07