I am currently integrating a C-Code (written by a third person) in a Simulink model. In the C-Code various sensor signals are filtered, using a PT1 filter with the following equation:
$$y(t) = \dfrac{u(t) + Cy(t-1)}{C + 1}$$
Where $y(t)$, $u(t)$ and $C$ are the output (the filtered signal), input and a factor applied for each signal individually, respectively.
Looking at the step function response, I can see a typical PT1-behaviour with a gain factor of 1.
I cannot figure out the derivation of this function from the general formulation (the differential equation) of a PT1, which is:
$$Ty'(t) + y(t) = Ku(t)$$
Can any of you guys help me out?
The equation being used in code is a discrete-time implementation of the filter. The second equation you gave is a continuous-time expression of the filter dynamics. In order to create a discrete-time filter from the continuous-time dynamics the person who wrote the code used a first order approximation (backwards difference, specifically) of the derivative of $y$, like so:
$$\frac{dy}{dt} \approx \frac{y(t)-y(t-\Delta t)}{\Delta t}$$
Now, if we use the notation $k$ to denote a sample taken at time $t$ and $k-1$ to denote a sample taken at time $t-\Delta t$, then we can derive the equation used in code as follows:
$$T\frac{dy}{dt} + y(t) = Ku(t)$$ $$T \frac{y(k)-y(k-1)}{\Delta t} + y(k) = Ku(k)$$ $$\left(\frac{T}{\Delta t} + 1\right) y(k) = K u(k) + \frac{T}{\Delta t} y(k-1)$$
Now let $K=1$ and $C = \frac{T}{\Delta t}$, and you get:
$$\left(C + 1\right) y(k) = u(k) + C y(k-1)$$ $$ y(k) = \frac{u(k) + C y(k-1)}{C + 1}$$
  • $\begingroup$ Thank you very much for your prompt answer. I have not thought about backwards difference this far, silly me :P This is exactly what I was looking for! $\endgroup$
    – J.M.
    Commented Jan 31, 2017 at 14:15