I am currently studying a boiler without many technical data.
Below a short description:
Fuel is put inside the boiler furnace. Primary (F1) and secondary air (F2) fans allow fresh air to go through the boiler. At the outlet of the gas circuit, there is also another fan (F3) at constant speed that is here to maintain a -300 Pa depressure inside the furnace. The fresh air temperature is increased up to 650°C thanks to combustion.
After combustion, hot air calories are exchanged with oil circulating along a coil inside the boiler. This oil is at 100°C before exchange, and at the end of the exchange, it is around 200°C and air temperature is around 250°C. The whole purpose of this boiler is to maintain this 200°C temperature of oil.
For security measures, a controller is here to ensure that the depressure on air side, inside the furnace remains constant by adjusting the primary and secondary air fans speed. Also, if oil temperature goes beyond 200°C, no more fuel will be added inside the boiler. A pressure decrease will increase these fans speed, and a pressure increase will decrease it.
So, for the heat exchange we have these values:
- Air flowrate: $\dot{m}_{air} = 100.000 kg/h$
- Air temp in: $T_{air1} = 650°C$
- Air temp out: $T_{air2} = 250°C$
- Specific heat of air: $C_{p_{air}} = 1.063 kJ/kg.K$
- Oil flowrate: $\dot{m}_{oil} = 212.600 kg/h$
- Oil temp in: $T_{oil1} = 100°C$
- Oil temp out: $T_{oil2} = 200°C$
- Specific heat of oil: $C_{p_{oil}} = 2 kJ/kg.K$
Thanks to this formula, we can estimate the heat exchange power (11,8 MW):
$$\dot{Q} = \dot{m}_{air}\cdot C_{p_{air}}\cdot (T_{air1}- T_{air2}) = \dot{m}_{oil}\cdot C_{p_{oil}}\cdot (T_{oil2} - T_{oil1}) $$
Now, I would like to predict the boiler bevahiour if I change 1 parameter: inlet oil temperature. As stated above, it is currently at 100°C before exchange. Now, let's say it is lower: 50°C.
What would happen?
Knowing from experience that we have a little margin regarding the heat exchange power capacity, my guess is that more fuel will be consumed to increase gas temperature and allow the oil outlet temperature to remain at 200°C. Though, pressure inside the boiler will most likely increase because of hotter air and the fans F1 and F2 will consequently end up running slower to maintain the set depressure. This would mean that we would get hotter air, but at a lesser quantity.
Though, if we manage to get as much air as before with a hotter air temperature, I would then think that oil will absorb the extra calories, leaving the outlet air temperature as it is.
Please let me know if you think that I am on the right path. I am pretty uncertain of this because I do not know the limitations of the boiler.
So, I would like to check all of this with calculation. I thought of following these steps:
- Find the surface area thanks to LMTD method
- Trying to use the NTU method to find the outlet temperatures
- Predicting the resulting pressure with perfect gas law inside the boiler to understand how the controller will manage fans F1 and F2
I am really uncertain on how to go through these steps though. LMTD method is ok, I found 72 m² of surface area, but after this, I am stuck.
I am not sure how to use NTU method and perfect gas law for this. For the volume part, should I consider the volume of the boiler, of the air volume going through it?